Table 3-4. Storage Management Messages
Event ID
|
Description
|
Severity
|
Cause and Action
|
Related Alert Information
|
SNMP Trap Numbers
|
2048
|
Device failed
|
Critical / Failure / Error
|
Cause: A storage component such as a physical disk or an enclosure has failed. The failed component may have been identified by the controller while performing a task such as a rescan or a check consistency.
Action: Replace the failed component. You can identify which disk has failed by locating the disk that has a red "X" for its status. Perform a rescan after replacing the failed component.
|
Clear Alert Number: 2121
Related Alert Number: 2095, 2201, 2203
Local Response Agent (LRA) Number: 2051, 2061, 2071, 2081, 2091, 2101
|
754 804 854 904 954 1004 1054 1104 1154 1204
|
2049
|
Physical disk removed
|
Warning / Non-critical
|
Cause: A physical disk has been removed from the disk group. This alert can also be caused by loose or defective cables or by problems with the enclosure.
Action: If a physical disk was removed from the disk group, either replace the disk or restore the original disk. On some controllers, a removed disk has a red X for its status. On other controllers, a removed disk may have an Offline status or is not displayed on the user interface. Perform a rescan after replacing or restoring the disk. If a disk has not been removed from the disk group, then check for problems with the cables. See the online help for more information on checking the cables. Ensure that the enclosure is powered on. If the problem persists, check the enclosure documentation for further diagnostic information.
|
Clear Alert Number: 2052
Related Alert Number: 2054, 2057, 2056, 2076, 2079, 2081, 2083, 2129, 2202, 2204, 2270, 2292, 2299, 2369
LRA Number: 2070
|
903
|
2050
|
Physical disk offline
|
Warning / Non-critical
|
Cause: A physical disk in the disk group is offline. The user may have manually put the physical disk offline.
Action: Perform a rescan. You can also select the offline disk and perform a Make Online operation.
|
Clear Alert Number: 2158
Related Alert Number: 2099, 2196
LRA Number: 2070
|
903
|
2051
|
Physical disk degraded
|
Warning / Non-critical
|
Cause: A physical disk has reported an error condition and may be degraded. The physical disk may have reported the error condition in response to a SMART Trip (Predictive Failure).
Action: Replace the degraded physical disk. You can identify which disk is degraded by locating the disk that has a Yellow Triangle for its status. Perform a rescan after replacing the disk.
|
Clear Alert: None
Related Alert Number: 2094
LRA Number: 2070
|
903
|
2052
|
Physical disk inserted
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert Number: 2065, 2305, 2367
LRA Number: None
|
901
|
2053
|
Virtual disk created
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2054
|
Virtual disk deleted
|
Warning / Non-critical
|
Cause: A virtual disk has been deleted. Performing a Reset Configuration may detect that a virtual disk has been deleted.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: 2080
|
1203
|
2055
|
Virtual disk configuration changed
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2056
|
Virtual disk failed
|
Critical / Failure / Error
|
Cause: One or more physical disks included in the virtual disk have failed. If the virtual disk is non-redundant (does not use mirrored or parity data), then the failure of a single physical disk can cause the virtual disk to fail. If the virtual disk is redundant, then more physical disks have failed than can be rebuilt using mirrored or parity information.
Action: Create a new virtual disk and restore from a backup.
|
Clear Alert: None
Related Alert Number: 2048, 2049, 2050, 2076, 2079, 2081, 2129, 2346
LRA Number: 2081
|
1204
|
2057
|
Virtual disk degraded
|
Warning / Non-critical
|
Cause 1: This alert message occurs when a physical disk included in a redundant virtual disk fails. Because the virtual disk is redundant (uses mirrored or parity information) and only one physical disk has failed, the virtual disk can be rebuilt.
Action 1: Replace the failed drive. Rebuild of the virtual disk starts automatically.
NOTE: If you put the drive in a different slot, you need to assign it as a hot spare for the rebuild to start automatically.
If you are using an Expandable RAID Controller (PERC) PERC 4/SC, 4/DC, 4e/DC, 4/Di, CERC ATA100/4ch, PERC 5/E, PERC 5/i or a Serial Attached SCSI (SAS) 5/iR controller, rebuild the virtual disk by first configuring a hot spare for the disk, and then initiating a write operation to the disk. The write operation initiates a rebuild of the disk.
Cause 2: A physical disk in the disk group has been removed.
Action 2: If a physical disk was removed from the disk group, either replace the disk or restore the original disk. You can identify which disk has been removed by locating the disk that has a red "X" for its status. Perform a rescan after replacing the disk.
|
Clear Alert Number: None
Related Alert Number: 2048, 2049, 2050, 2076, 2079, 2081, 2123, 2129, 2346
LRA Number: 2080
|
1203
|
2058
|
Virtual disk check consistency started
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2085.
Related Alert Number: None
LRA Number: None
|
1201
|
2059
|
Virtual disk format started
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2086.
Related Alert Number: None
LRA Number: None
|
1201
|
2060
|
Copy of data started from physical disk %2 to physical disk %1.
|
OK / Normal /Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: 2075
LRA Number: None
|
1201
|
2061
|
Virtual disk initialization started
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2088
Related Alert Number: None
LRA Number: None
|
1201
|
2062
|
Physical disk initialization started
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2089
Related Alert Number: None
LRA Number: None
|
901
|
2063
|
Virtual disk reconfiguration started
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2090
Related Alert Number: None
LRA Number: None
|
1201
|
2064
|
Virtual disk rebuild started
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2091
Related Alert Number: None
LRA Number: None
|
1201
|
2065
|
Physical disk rebuild started
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2092
Related Alert Number: 2099, 2121, 2196
LRA Number: None
|
901
|
2067
|
Virtual disk check consistency cancelled
|
OK / Normal / Informational
|
Cause: The check consistency operation was cancelled because a physical disk in the array has failed or because a user cancelled the check consistency operation.
Action: If the physical disk failed, then replace the physical disk. You can identify which disk failed by locating the disk that has a red "X" for its status. Perform a rescan after replacing the disk. The consistency check can take a long time. The time it takes depends on the size of the physical disk or the virtual disk.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
1201
|
2070
|
Virtual disk initialization cancelled
|
OK / Normal / Informational
|
Cause: The virtual disk initialization cancelled because a physical disk included in the virtual disk has failed or because a user cancelled the virtual disk initialization.
Action: If a physical disk failed, then replace the physical disk. You can identify which disk has failed by locating the disk that has a red "X" for its status. Perform a rescan after replacing the disk. Restart the format physical disk operation. Restart the virtual disk initialization.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
1201
|
2074
|
Physical disk rebuild cancelled
|
OK / Normal / Informational
|
Cause: The user has cancelled the rebuild operation.
Action: Restart the rebuild operation.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
901
|
2075
|
Copy of data completed from physical disk %2 to physical disk %1.
|
OK / Normal / Informational
|
Cause: This alert is provided for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: 2060
LRA Number: None
|
1201
|
2076
|
Virtual disk Check Consistency failed
|
Critical / Failure / Error
|
Cause: A physical disk included in the virtual disk failed or there is an error in the parity information. A failed physical disk can cause errors in parity information.
Action: Replace the failed physical disk. You can identify which disk has failed by locating the disk that has a red "X" for its status. Rebuild the physical disk. When finished, restart the check consistency operation.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2081
|
1204
|
2077
|
Virtual disk format failed.
|
Critical / Failure / Error
|
Cause: A physical disk included in the virtual disk failed.
Action: Replace the failed physical disk. You can identify which physical disk has failed by locating the disk that has a red X for its status. Rebuild the physical disk. When finished, restart the virtual disk format operation.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2081
|
1204
|
2079
|
Virtual disk initialization failed.
|
Critical / Failure / Error
|
Cause: A physical disk included in the virtual disk has failed or a user has cancelled the initialization.
Action: If a physical disk has failed, then replace the physical disk.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2081
|
1204
|
2080
|
Physical disk initialization failed
|
Critical / Failure / Error
|
Cause: The physical disk has failed or is not functioning.
Action: Replace the failed or non-functional disk. You can identify a disk that has failed by locating the disk that has a red "X" for its status. Restart the initialization.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2071
|
904
|
2081
|
Virtual disk reconfiguration failed
|
Critical / Failure / Error
|
Hardware RAID:
Cause: A physical disk included in the virtual disk has failed or is not functioning. A user may also have cancelled the reconfiguration.
Action: Replace the failed or non-functional disk. You can identify a disk that has failed by locating the disk that displays a red X in the status field.
If the physical disk is part of a redundant array, then rebuild the physical disk. When finished, restart the reconfiguration.
Software RAID:
•
|
Perform a backup with the Verify option.
|
•
|
If the file backup fails, try to restore the failed file from a previous backup.
|
•
|
When the backup with the Verify option is complete without any errors, delete the Virtual Disk.
|
•
|
Recreate a new Virtual Disk with new drives.
|
•
|
Restore the data from backup.
|
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2081
|
1204
|
2082
|
Virtual disk rebuild failed
|
Critical / Failure / Error
|
Cause: A physical disk included in the virtual disk has failed or is not functioning. A user may also have cancelled the rebuild.
Action: Replace the failed or non-functional disk. You can identify a disk that has failed by locating the disk that has a red "X" for its status. Restart the virtual disk rebuild.
|
Clear Alert Number: None
Related Alert Number: 2048
LRA Number: 2081
|
1204
|
2083
|
Physical disk rebuild failed
|
Critical / Failure / Error
|
Cause: A physical disk included in the virtual disk has failed or is not functioning. A user may also have cancelled the rebuild.
Action: Replace the failed or non-functional disk. You can identify a disk that has failed by locating the disk that has a red "X" for its status. Rebuild the virtual disk rebuild.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2071
|
904
|
2085
|
Virtual disk check consistency completed
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2085 is a clear alert for alert 2058.
Related Alert Number: None
LRA Number: None
|
1201
|
2086
|
Virtual disk format completed
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2086 is a clear alert for alert 2059.
Related Alert Number: None
LRA Number: None
|
1201
|
2087
|
Copy of data resumed from physical disk %2 to physical disk %1
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: None
Related Alert Number: 2060
LRA Number: None
|
901
|
2088
|
Virtual disk initialization completed
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2088 is a clear alert for alerts 2061 and 2136.
Related Alert Number: None
LRA Number: None
|
1201
|
2089
|
Physical disk initialization completed
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2089 is a clear alert for alert 2062.
Related Alert Number: None
LRA Number: None
|
901
|
2090
|
Virtual disk reconfiguration completed
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2090 is a clear alert for alert 2063.
Related Alert Number: None
LRA Number: None
|
1201
|
2091
|
Virtual disk rebuild completed
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2091 is a clear alert for alert 2064.
Related Alert Number: None
LRA Number: None
|
1201
|
2092
|
Physical disk rebuild completed
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2092 is a clear alert for alert 2065.
Related Alert Number: None
LRA Number: None
|
901
|
2094
|
Predictive Failure reported.
|
Warning / Non-critical
|
Cause: The physical disk is predicted to fail. Many physical disks contain Self Monitoring Analysis and Reporting Technology (SMART). When enabled, SMART monitors the health of the disk based on indications such as the number of write operations that have been performed on the disk.
Action: Replace the physical disk. Even though the disk may not have failed yet, it is strongly recommended that you replace the disk.
If this disk is part of a redundant virtual disk, perform the Offline task on the disk; replace the disk; the rebuild starts automatically.
NOTE: If you put the drive in a different slot, you need to assign it as a hot spare for the rebuild to start automatically.
If this disk is a hot spare, then unassign the hot spare; perform the Prepare to Remove task on the disk; replace the disk; and assign the new disk as a hot spare.
|
CAUTION:
If this disk is part of a non-redundant disk, back up your data immediately. If the disk fails, you cannot recover the data.
|
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2070
|
903
|
2095
|
SCSI sense data %1.
|
OK / Normal / Informational
|
Cause: A SCSI device experienced an error, but may have recovered.
Action: None
|
Clear Alert Number: None
Related Alert Number: 2273
LRA Number: None
|
751, 851, 901
|
2098
|
Global hot spare assigned
|
OK / Normal / Informational
|
Cause: A user has assigned a physical disk as a global hot spare. This alert is for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: 2277
LRA Number: None
|
901
|
2099
|
Global hot spare unassigned
|
OK / Normal / Informational
|
Cause: A physical disk that was assigned as a hot spare has been unassigned and is no longer functioning as a hot spare. The physical disk may have been unassigned by a user or automatically unassigned by Storage Management. Storage Management unassigns hot spares that have been used to rebuild data. Once data is rebuilt, the hot spare becomes a member of the virtual disk and is no longer assigned as a hot spare. You need to assign a new hot spare to maintain data protection in this situation. On the CERC SATA1.5/6ch, and CERC SATA1.5/2s controllers, if you use another application such as the BIOS to include a hot spare in a virtual disk, then Storage Management unassigns the physical disk as a hot spare.
Action: Although this alert is provided for informational purposes, you may need to assign a new hot spare to the virtual disk.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
901
|
2100
|
Temperature exceeded the maximum warning threshold
|
Warning / Non-critical
|
Cause: The physical disk enclosure is too hot. A variety of factors can cause the excessive temperature. For example, a fan may have failed, the thermostat may be set too high, or the room temperature may be too hot.
Action: Check for factors that may cause overheating. For example, verify that the enclosure fan is working. You should also check the thermostat settings and examine whether the enclosure is located near a heat source. Make sure the enclosure has enough ventilation and that the room temperature is not too hot. See the physical disk enclosure documentation for more diagnostic information.
|
Clear Alert Number: 2353
Related Alert Number: 2112
LRA Number: 2090
|
1053
|
2101
|
Temperature dropped below the minimum warning threshold
|
Warning / Non-critical
|
Cause: The physical disk enclosure is too cool.
Action: Check if the thermostat setting is too low and if the room temperature is too cool.
|
Clear Alert Number: 2353
Related Alert Number: None
LRA Number: 2090
|
1053
|
2102
|
Temperature exceeded the maximum failure threshold
|
Critical / Failure / Error
|
Cause: The physical disk enclosure is too hot. A variety of factors can cause the excessive temperature. For example, a fan may have failed, the thermostat may be set too high, or the room temperature may be too hot.
Action: Check for factors that may cause overheating. For example, verify that the enclosure fan is working. You should also check the thermostat settings and examine whether the enclosure is located near a heat source. Make sure the enclosure has enough ventilation and that the room temperature is not too hot. See the physical disk enclosure documentation for more diagnostic information.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2091
|
1054
|
2103
|
Temperature dropped below the minimum failure threshold
|
Critical / Failure / Error
|
Cause: The physical disk enclosure is too cool.
Action: Check if the thermostat setting is too low and if the room temperature is too cool.
|
Clear Alert Number: None
Related Alert Number: 2112
LRA Number: 2091
|
1054
|
2104
|
Controller battery is reconditioning
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2105
Related Alert Number: None
LRA Number: None
|
1151
|
2105
|
Controller battery recondition is completed
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2105 is a clear alert for alert 2104.
Related Alert Number: None
LRA Number: None
|
1151
|
2106
|
SMART FPT exceeded
|
Warning / Non-critical
|
Cause: A disk on the specified controller has received a SMART alert (predictive failure) indicating that the disk is likely to fail in the near future.
Action: Replace the disk that has received the SMART alert. If the physical disk is a member of a non-redundant virtual disk, then back up the data before replacing the disk.
|
CAUTION:
Removing a physical disk that is included in a non-redundant virtual disk causes the virtual disk to fail and may cause data loss.
|
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2070
|
903
|
2107
|
SMART configuration change
|
Critical / Failure / Error
|
Cause: A disk has received a SMART alert (predictive failure) after a configuration change. The disk is likely to fail in the near future.
Action: Replace the disk that has received the SMART alert. If the physical disk is a member of a non-redundant virtual disk, then back up the data before replacing the disk.
|
CAUTION:
Removing a physical disk that is included in a non-redundant virtual disk causes the virtual disk to fail and may cause data loss.
|
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2071
|
904
|
2108
|
SMART warning
|
Warning / Non-critical
|
Cause: A disk has received a SMART alert (predictive failure). The disk is likely to fail in the near future.
Action: Replace the disk that has received the SMART alert. If the physical disk is a member of a non-redundant virtual disk, then back up the data before replacing the disk.
|
CAUTION:
Removing a physical disk that is included in a non-redundant virtual disk causes the virtual disk to fail and may cause data loss.
|
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2070
|
903
|
2109
|
SMART warning temperature
|
Warning / Non-critical
|
Cause: A disk has reached an unacceptable temperature and received a SMART alert (predictive failure). The disk is likely to fail in the near future.
Action 1: Determine why the physical disk has reached an unacceptable temperature. A variety of factors can cause the excessive temperature. For example, a fan may have failed, the thermostat may be set too high, or the room temperature may be too hot or cold. Verify that the fans in the server or enclosure are working. If the physical disk is in an enclosure, you should check the thermostat settings and examine whether the enclosure is located near a heat source.
Make sure the enclosure has enough ventilation and that the room temperature is not too hot. See the physical disk enclosure documentation for more diagnostic information.
Action 2: If you cannot identify why the disk has reached an unacceptable temperature, then replace the disk. If the physical disk is a member of a non-redundant virtual disk, then back up the data before replacing the disk.
|
CAUTION:
Removing a physical disk that is included in a non-redundant virtual disk causes the virtual disk to fail and may cause data loss.
|
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2070
|
903
|
2110
|
SMART warning degraded
|
Warning / Non-critical
|
Cause: A disk is degraded and has received a SMART alert (predictive failure). The disk is likely to fail in the near future.
Action: Replace the disk that has received the SMART alert. If the physical disk is a member of a non-redundant virtual disk, then back up the data before replacing the disk.
|
CAUTION:
Removing a physical disk that is included in a non-redundant virtual disk causes the virtual disk to fail and may cause data loss.
|
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2070
|
903
|
2111
|
Failure prediction threshold exceeded due to test
|
Warning / Non-critical
|
Cause: A disk has received a SMART alert (predictive failure) due to test conditions.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2070
|
903
|
2112
|
Enclosure was shut down
|
Critical / Failure / Error
|
Cause: The physical disk enclosure is either hotter or cooler than the maximum or minimum allowable temperature range.
Action: Check for factors that may cause overheating or excessive cooling. For example, verify that the enclosure fan is working. You should also check the thermostat settings and examine whether the enclosure is located near a heat source. Make sure the enclosure has enough ventilation and that the room temperature is not too hot or too cold. See the enclosure documentation for more diagnostic information.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2091
|
854
|
2114
|
A consistency check on a virtual disk has been paused (suspended)
|
OK / Normal / Informational
|
Cause: The check consistency operation on a virtual disk was paused by a user.
Action: To resume the check consistency operation, right-click the virtual disk in the tree view and select Resume Check Consistency.
|
Clear Alert Number: 2115
Related Alert Number: None
LRA Number: None
|
1201
|
2115
|
A consistency check on a virtual disk has been resumed
|
OK / Normal / Informational
|
Cause: The check consistency operation on a virtual disk has resumed processing after being paused by a user. This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2115 is a clear alert for alert 2114.
Related Alert Number: None
LRA Number: None
|
1201
|
2116
|
A virtual disk and its mirror have been split
|
OK / Normal / Informational
|
Cause: A user has caused a mirrored virtual disk to be split. When a virtual disk is mirrored, its data is copied to another virtual disk in order to maintain redundancy. After being split, both virtual disks retain a copy of the data although the mirror is no longer intact. The updates to the data are no longer copied to the mirror. This alert is for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
1201
|
2117
|
A mirrored virtual disk has been unmirrored
|
OK / Normal / Informational
|
Cause: A user has caused a mirrored virtual disk to be unmirrored. When a virtual disk is mirrored, its data is copied to another virtual disk in order to maintain redundancy. After being unmirrored, the disk formerly used as the mirror returns to being a physical disk and becomes available for inclusion in another virtual disk. This alert is for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
1201
|
2118
|
Change write policy
|
OK / Normal / Informational
|
Cause: A user has changed the write policy for a virtual disk. This alert is for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
1201
|
2120
|
Enclosure firmware mismatch
|
Warning / Non-critical
|
Cause: The firmware on the EMM is not the same version. It is required that both modules have the same version of the firmware. This alert may be caused when a user attempts to insert an EMM module that has a different firmware version than an existing module.
Action: Download the same version of the firmware to both EMM modules.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2090
|
853
|
2121
|
Device returned to normal
|
OK / Normal / Informational
|
Cause: A device that was previously in an error state has returned to a normal state. For example, if an enclosure became too hot and subsequently cooled down, you may receive this alert. This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2121 is a clear alert for alert 2048.
Related Alert Number: 2050, 2065, 2158
LRA Number: None
|
752 802 852 902 952 1002 1052 1102 1152 1202
|
2122
|
Redundancy degraded
|
Warning / Non-critical
|
Cause: One or more of the enclosure components has failed.
For example, a fan or power supply may have failed. Although the enclosure is currently operational, the failure of additional components could cause the enclosure to fail.
Action: Identify and replace the failed component. To identify the failed component, select the enclosure in the tree view and click the Health subtab. Any failed component is identified with a red X on the enclosure's Health subtab. Alternatively, you can select the Storage object and click the Health subtab.
The controller status displayed on the Health subtab indicates whether a controller has a Failed or Degraded component.
See the enclosure documentation for information on replacing enclosure components and for other diagnostic information.
|
Clear Alert Status: 2124
Related Alert Number: 2048
LRA Number: 2090
|
1305
|
2123
|
Redundancy lost
|
Warning / Non-critical
|
Cause: A virtual disk or an enclosure has lost data redundancy. In the case of a virtual disk, one or more physical disks included in the virtual disk have failed. Due to the failed physical disk or disks, the virtual disk is no longer maintaining redundant (mirrored or parity) data. The failure of an additional physical disk results in lost data. In the case of an enclosure, more than one enclosure component has failed. For example, the enclosure may have suffered the loss of all fans or all power supplies.
Action: Identify and replace the failed components. To identify the failed component, select the Storage object and click the Health subtab.
The controller status displayed on the Health subtab indicates whether a controller has a Failed or Degraded component.
Click the controller that displays a Warning or Failed status. This action displays the controller Health subtab which displays the status of the individual controller components. Continue clicking the components with a Warning or Health status until you identify the failed component.
See the online help for more information. See the enclosure documentation for information on replacing enclosure components and for other diagnostic information.
|
Clear Alert Number: 2124
Related Alert Number: 2048, 2049, 2057
LRA Number: 2080, 2090
|
1306
|
2124
|
Redundancy normal
|
OK / Normal / Informational
|
Cause: Data redundancy has been restored to a virtual disk or an enclosure that previously suffered a loss of redundancy. This alert is for informational purposes.
Action: None
|
Clear Alert Number: Alert 2124 is a clear alert for alerts 2122 and 2123.
Related Alert Number: None
LRA Number: None
|
1304
|
2125
|
Controller cache preserved for missing or offline virtual disk
|
Warning / Non-critical
|
Cause: Virtual disk controller was disconnected, during I/O operation.
Action: Import foreign disks, if any. Check if the enclosure containing the virtual disk is disconnected from the controller.
|
Clear Alert Number: 2186, 2240
Related Alert Number: None
LRA Number: None
|
1203
|
2126
|
SCSI sense sector reassign
|
Warning / Non-critical
|
Cause: A sector of the physical disk is corrupted and data cannot be maintained on this portion of the disk. This alert is for informational purposes.
|
CAUTION:
Any data residing on the corrupt portion of the disk may be lost and you may need to restore your data from backup.
|
Action: If the physical disk is part of a non-redundant virtual disk, then back up the data and replace the physical disk.
|
CAUTION:
Removing a physical disk that is included in a non-redundant virtual disk causes the virtual disk to fail and may cause data loss.
|
If the disk is part of a redundant virtual disk, then any data residing on the corrupt portion of the disk is reallocated elsewhere in the virtual disk.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
903
|
2127
|
Background initialization (BGI) started
|
OK / Normal / Informational
|
Cause: BGI of a virtual disk has started. This alert is for informational purposes.
Action: None
|
Clear Alert Status: 2130
Related Alert Number: None
LRA Number: None
|
1201
|
2128
|
BGI cancelled
|
OK / Normal / Informational
|
Cause: BGI of a virtual disk has been cancelled. A user or the firmware may have stopped BGI.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
1201
|
2129
|
BGI failed
|
Critical / Failure / Error
|
Cause: BGI of a virtual disk has failed.
Action: None
|
Clear Alert Number: None
Related Alert Number: 2340
LRA Number: 2081
|
1204
|
2130
|
BGI completed
|
OK / Normal / Informational
|
Cause: BGI of a virtual disk has completed. This alert is for informational purposes.
Action: None
|
Clear Alert Number: Alert 2130 is a clear alert for alert 2127.
Related Alert Number: None
LRA Number: None
|
1201
|
2131
|
Firmware version mismatch
|
Warning / Non-critical
|
Cause: The firmware on the controller is not a supported version.
Action: Install a supported version of the firmware. If you do not have a supported version of the firmware available, check with your support provider for information on how to obtain the most current firmware.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2060
|
753
|
2132
|
Driver version mismatch
|
Warning / Non-critical
|
Cause: The controller driver is not a supported version.
Action: Install a supported version of the driver. If you do not have a supported driver version available, you can check with your support provider for information on how to obtain the most current driver.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2060
|
753
|
2135
|
Array Manager is installed on the system
NOTE: This is not supported on Server Administrator version 6.0.1.
|
Warning / Non-critical
|
Cause: Storage Management has been installed on a system that has an Array Manager installation.
Action: Installing Storage Management and Array Manager on the same system is not a supported configuration. Uninstall either Storage Management or Array Manager.
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: 2050
|
103
|
2136
|
Virtual disk initialization
|
OK / Normal / Informational
|
Cause: Virtual disk initialization is in progress. This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2088
Related Alert Number: None
LRA Number: None
|
1201
|
2137
|
Communication timeout
|
Warning / Non-critical
|
Cause: The controller is unable to communicate with an enclosure. There are several reasons why communication may be lost. For example, there may be a bad or loose cable. An unusual amount of I/O may also interrupt communication with the enclosure. In addition, communication loss may be caused by software, hardware, or firmware problems, bad or failed power supplies, and enclosure shutdown.
When viewed in the alert log, the description for this event displays several variables. These variables are: controller and enclosure names, type of communication problem, return code, and SCSI status.
Action: Check for problems with the cables. See the online help for more information on checking the cables. You should also check to see if the enclosure has degraded or failed components. To do so, select the enclosure object in the tree view and click the Health subtab. The Health subtab displays the status of the enclosure components. Verify that the controller has supported driver and firmware versions installed and that the EMMs are each running the same version of supported firmware.
|
Clear Alert Number: 2162
Related Alert Number: None
LRA Number: 2090
|
853
|
2138
|
Enclosure alarm enabled
|
OK / Normal / Informational
|
Cause: A user has enabled the enclosure alarm. This alert is for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
851
|
2139
|
Enclosure alarm disabled
|
OK / Normal / Informational
|
Cause: A user has disabled the enclosure alarm.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
851
|
2140
|
Dead disk segments restored
|
OK / Normal / Informational
|
Cause: Disk space that was formerly "dead" or inaccessible to a redundant virtual disk has been restored. This alert is for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
1201
|
2141
|
Physical disk dead segments removed.
|
OK / Normal / Informational
|
Cause: Portions of the physical disk were formerly inaccessible. The disk space from these dead segments has been recovered and is now usable. Any data residing on these dead segments has been lost. This alert is for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
901
|
2142
|
Controller rebuild rate has changed
|
OK / Normal / Informational
|
Cause: A user has changed the controller rebuild rate. This alert is for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
751
|
2143
|
Controller alarm enabled
|
OK / Normal / Informational
|
Cause: A user has enabled the controller alarm. This alert is for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
751
|
2144
|
Controller alarm disabled
|
OK / Normal / Informational
|
Cause: A user has disabled the controller alarm. This alert is for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
751
|
2145
|
Controller battery low
|
Warning / Non-critical
|
Cause: The controller battery charge is low.
Action: Recondition the battery. See the online help for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2100
|
1153
|
2146
|
Bad block replacement error
|
Warning / Non-critical
|
Cause: A portion of a physical disk is damaged.
Action: See the Server Administrator Storage Management online help for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2147
|
Bad block sense error
|
Warning / Non-critical
|
Cause: A portion of a physical disk is damaged.
Action: See the Server Administrator Storage Management online help for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2148
|
Bad block medium error
|
Warning / Non-critical
|
Cause: A portion of a physical disk is damaged.
Action: See the Server Administrator Storage Management online help for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2149
|
Bad block extended sense error
|
Warning / Non-critical
|
Cause: A portion of a physical disk is damaged.
Action: See the Server Administrator Storage Management online help for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2150
|
Bad block extended medium error
|
Warning / Non-critical
|
Cause: A portion of a physical disk is damaged.
Action: See the Server Administrator Storage Management online help for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2151
|
Enclosure asset tag changed
|
OK / Normal / Informational
|
Cause: A user has changed the enclosure asset tag. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
851
|
2152
|
Enclosure asset name changed
|
OK / Normal / Informational
|
Cause: A user has changed the enclosure asset name. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
851
|
2153
|
Enclosure service tag changed
|
OK / Normal / Informational
|
Cause: An enclosure service tag was changed. In most circumstances, this service tag should only be changed by your service provider.
Action: Ensure that the tag was changed under authorized circumstances.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
851
|
2154
|
Maximum temperature probe warning threshold value changed
|
OK / Normal / Informational
|
Cause: A user has changed the value for the maximum temperature probe warning threshold. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1051
|
2155
|
Minimum temperature probe warning threshold value changed
|
OK / Normal / Informational
|
Cause: A user has changed the value for the minimum temperature probe warning threshold. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1051
|
2156
|
Controller alarm has been tested
|
OK / Normal / Informational
|
Cause: The controller alarm test has run successfully. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2157
|
Controller configuration has been reset
|
OK / Normal / Informational
|
Cause: A user has reset the controller configuration. See the online help for more information. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2158
|
Physical disk online
|
OK / Normal / Informational
|
Cause: An offline physical disk has been made online. This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2158 is a clear alert for alert 2050.
Related Alert Number: 2048, 2050, 2065, 2099, 2121, 2196, 2201, 2203
LRA Number: None
|
901
|
2159
|
Virtual disk renamed
|
OK / Normal / Informational
|
Cause: A user has renamed a virtual disk.
When renaming a virtual disk on a PERC 4/SC, 4/DC, 4e/DC, 4/Di, CERC ATA100/4ch, PERC 5/E, PERC 5/i or SAS 5/iR controller, this alert displays the new virtual disk name.
On the PERC 4/SC, 4/DC, 4e/DC, 4/Di, 4/IM, 4e/Si, 4e/Di, and CERC ATA 100/4ch controllers, this alert displays the original virtual disk name. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2160
|
Dedicated hot spare assigned
|
OK / Normal / Informational
|
Cause: A user has assigned a physical disk as a dedicated hot spare to a virtual disk. This alert is provided for informational purposes.
Action: None
|
Clear Alert: 2161
Related Alert: None
LRA Number: None
|
901
|
2161
|
Dedicated hot spare unassigned
|
OK / Normal / Informational
|
Cause: A physical disk that was assigned as a hot spare has been unassigned and is no longer functioning as a hot spare. The physical disk may have been unassigned by a user or automatically unassigned by Storage Management. Storage Management unassigns hot spares that have been used to rebuild data. Once data is rebuilt onto the hot spare, the hot spare becomes a member of the virtual disk and is no longer assigned as a hot spare. You need to assign a new hot spare to maintain data protection in this situation. On the CERC SATA1.5/6ch, and CERC SATA1.5/2s controllers, if you use another application such as the BIOS to include a hot spare in a virtual disk, then Storage Management unassigns the physical disk as a hot spare.
Action: Although this alert is provided for informational purposes, you may need to assign a new hot spare to the virtual disk.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2162
|
Communication regained
|
OK / Normal / Informational
|
Cause: Communication with an enclosure has been restored. This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2162 is a clear alert for alerts 2137 and 2292.
Related Alert: None
LRA Number: None
|
851
|
2163
|
Rebuild completed with errors
|
Critical / Failure / Error
|
Cause: During a rebuild one or more blocks of data was not recoverable due to missing parity information. Some data loss may have occurred..
Action: Perform a check to verify the built array. Any files that are impacted should be restored from a backup. See the Storage Management online help for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2071
|
904
|
2164
|
See the Readme file for a list of validated controller driver versions
|
OK / Normal / Informational
|
Cause: Storage Management is unable to determine whether the system has the minimum required versions of the RAID controller drivers. This alert is for informational purposes.
Action: See the Readme file for driver and firmware requirements. In particular, if Storage Management experiences performance problems, you should verify that you have the minimum supported versions of the drivers and firmware installed.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
101
|
2165
|
The RAID controller firmware and driver validation was not performed. The configuration file cannot be opened.
|
Warning / Non-critical
|
Cause: Storage Management is unable to determine whether the system has the minimum required versions of the RAID controller firmware and drivers. This situation may occur for a variety of reasons. For example, the installation directory path to the configuration file may not be correct. The configuration file may also have been removed or renamed.
Action: Reinstall Storage Management
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2166
|
The RAID controller firmware and driver validation was not performed. The configuration file is out of date, missing the required information, or not properly formatted to complete the comparison.
|
Warning / Non-critical
|
Cause: Storage Management is unable to determine whether the system has the minimum required versions of the RAID controller firmware and drivers. This situation has occurred because a configuration file is out of date, missing the required information, or not properly formatted to complete the comparison.
Action: Reinstall Storage Management.
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2167
|
The current kernel version and the non-RAID SCSI driver version are older than the minimum required levels. See readme.txt for a list of validated kernel and driver versions.
|
Warning / Non-critical
|
Cause: The version of the kernel and the driver do not meet the minimum requirements. Storage Management may not be able to display the storage or perform storage management functions until you have updated the system to meet the minimum requirements.
Action: See the Readme file for a list of validated kernel and driver versions. Update the system to meet the minimum requirements and then reinstall Storage Management.
|
Clear Alert: None
Related Alert: None
LRA Number: 2050
|
103
|
2168
|
The non-RAID SCSI driver version is older than the minimum required level. See readme.txt for the validated driver version.
|
Warning / Non-critical
|
Cause: The version of the driver does not meet the minimum requirements. Storage Management may not be able to display the storage or perform storage management functions until you have updated the system to meet the minimum requirements.
Action: See the Readme file for the validated driver version. Update the system to meet the minimum requirements and then reinstall Storage Management.
|
Clear Alert: None
Related Alert: None
LRA Number: 2050
|
103
|
2169
|
The controller battery needs to be replaced.
|
Critical / Failure / Error
|
Cause: The controller battery cannot be recharged. The battery may be old or it may have been already recharged the maximum number of times. In addition, the battery charger may not be working.
Action: Replace the battery pack.
|
Clear Alert: None
Related Alert Number: 2118
LRA Number: 2101
|
1154
|
2170
|
The controller battery charge level is normal.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2171
|
The controller battery temperature is above normal.
|
Warning / Non-critical
|
Cause: The battery may be recharging, the room temperature may be too hot, or the fan in the system may be degraded or failed.
Action: If this alert was generated due to a battery recharge, the situation is corrected when the recharge is complete. You should also check if the room temperature is normal and that the system components are functioning properly.
|
Clear Alert Number: 2172
Related Alert: None
LRA Number: 2100
|
1153
|
2172
|
The controller battery temperature is normal.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2172 is a clear alert for alert 2171.
Related Alert: None
LRA Number: None
|
1151
|
2173
|
Unsupported configuration detected. The SCSI rates of the enclosure management modules (EMMs) are not the same. EMM0%1 EMM1%2
|
Warning / Non-critical
|
Cause: An unsupported configuration was detected.
Action: Replace one of the EMMs with the matching SCSI rate EMM.
|
Clear Alert: None
Related Alert: None
LRA Number: 2090
|
853
|
2174
|
The controller battery has been removed.
|
Warning / Non-critical
|
Cause: The controller cannot communicate with the battery. The battery may be removed, or the contact point between the controller and the battery may be burnt or corroded.
Action: Replace the battery if it has been removed. If the contact point between the battery and the controller is burnt or corroded, you must replace either the battery or the controller, or both. See the hardware documentation for information on how to safely access, remove, and replace the battery.
|
Clear Alert: None
Related Alert Number: 2188, 2318
LRA Number: 2100
|
1153
|
2175
|
The controller battery has been replaced.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2176
|
The controller battery Learn cycle has started.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2177
Related Alert: None
LRA Number: None
|
1151
|
2177
|
The controller battery Learn cycle has completed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2177 is a clear alert for alert 2176.
Related Alert: None
LRA Number: None
|
1151
|
2178
|
The controller battery Learn cycle has timed out.
|
Warning / Non-critical
|
Cause: The controller battery must be fully charged before the Learn cycle can begin. The battery may be unable to maintain a full charge causing the Learn cycle to timeout. Additionally, the battery must be able to maintain cached data for a specified period of time in the event of a power loss. For example, some batteries maintain cached data for 24 hours. If the battery is unable to maintain cached data for the required period of time, then the Learn cycle timeout occurs.
Action: Replace the battery pack as the battery is unable to maintain a full charge.
|
Clear Alert: None
Related Alert: None
LRA Number: 2100
|
1153
|
2179
|
The controller battery Learn cycle has been postponed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2180
|
The controller battery Learn cycle starts in %1 days.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes. The %1 indicates a substitution variable. The text for this substitution variable is displayed with the alert in the alert log and can vary depending on the situation.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2181
|
The controller battery learn cycle starts in %1 hours.
|
OK / Normal / Informational
|
Cause: The %1 indicates a substitution variable. The text for this substitution variable is displayed with the alert in the alert log and can vary depending on the situation. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2182
|
An invalid SAS configuration has been detected.
|
Critical / Failure / Error
|
Cause: The controller and attached enclosures are not cabled correctly.
Action: See the hardware documentation for information on correct cabling configurations.
|
Clear Alert: None
Related Alert: None
LRA Number: 2061
|
754
|
2183
|
Replace Member Operation failed on physical disk %1 from physical disk %2.
|
Critical / Failure / Error
|
Cause: The physical disk participating in the Replace Member Operation operation has failed.
Action: None
|
Clear Alert: None
Related Alert Number: 2060
LRA Number: None
|
904
|
2184
|
Physical disk Replace Member Operation cancelled.
|
OK / Normal / Informational
|
Cause: User cancelled the Replace Member Operation operation.
Action: None
|
Clear Alert Number: None
Related Alert Number: 2060
LRA Number: None
|
901
|
2185
|
Physical disk Replace Member Operation stopped for spare.
|
Warning/ Non-critical
|
Cause: This alert is provided for informational purposes
Action: None
|
Clear Alert Number: None
Related Alert Number: 2060
LRA Number: None
|
903
|
2186
|
The controller cache has been discarded.
|
Warning / Non-critical
|
Cause: The controller has flushed the cache and any data in the cache has been lost. This may happen if the system has memory or battery problems that cause the controller to distrust the cache. Although user data may have been lost, this alert does not always indicate that relevant or user data has been lost.
Action: Verify that the battery and memory are functioning properly.
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2187
|
Single-bit ECC error limit exceeded on the controller DIMM.
|
Warning / Non-critical
|
Cause: The system memory is malfunctioning.
Action: Contact technical support to replace the controller memory.
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2188
|
The controller write policy has been changed to Write Through.
|
OK / Normal / Informational
|
Cause: The controller battery is unable to maintain cached data for the required period of time. For example, if the required period of time is 24 hours, the battery is unable to maintain cached data for 24 hours. It is normal to receive this alert during the battery Learn cycle as the Learn cycle discharges the battery before recharging it. When discharged, the battery cannot maintain cached data.
Action: Check the health of the battery. If the battery is weak, replace the battery pack.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2189
|
The controller write policy has been changed to Write Back.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2190
|
The controller has detected a hot-add of an enclosure.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2191
|
Multiple enclosures are attached to the controller. This is an unsupported configuration.
|
Critical / Failure / Error
|
Cause: There are too many enclosures attached to the controller port. When the enclosure limit is exceeded, the controller loses contact with all enclosures attached to the port.
Action: Remove the last enclosure. You must remove the enclosure that has been added last and is causing the enclosure limit to exceed.
|
Clear Alert: None
Related Alert Number: 2211
LRA Number: 2091
|
854
|
2192
|
The virtual disk Check Consistency has made corrections and completed.
|
Informational
|
Cause: The virtual disk Check Consistency has identified errors and made corrections. For example, the Check Consistency may have encountered a bad disk block and remapped the disk block to restore data consistency. This alert is for informational purposes.
Action: None. As a precaution, monitor the alert log for other errors related to this virtual disk. If problems persist, contact Technical Support.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1203
|
2193
|
The virtual disk reconfiguration has resumed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2194
|
The virtual disk Read policy has changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2195
|
Dedicated hot spare assigned. Physical disk %1
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2196
Related Alert: None
LRA Number: None
|
1201
|
2196
|
Dedicated hot spare unassigned. Physical disk %1
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: None
Related Alert: None
LRA Number: None
|
1201
|
2197
|
Physical disk Replace Member Operation stopped for rebuild.
|
Warning
|
Cause: This alert is provided for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: 2060
LRA Number: None
|
903
|
2198
|
The physical disk is too small to be used for Replace Member Operation.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: None
Related Alert Number: None
LRA Number: None
|
903
|
2199
|
The virtual disk cache policy has changed.
|
Warning
|
Cause: User has provided invalid input for the chosen operation.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2200
|
Replace Member Operation not possible as SAS/SATA is not supported in the same virtual disk.
|
Warning/ Non-critical
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
903
|
2201
|
A global hot spare failed.
|
Warning / Non-critical
|
Cause: The controller is not able to communicate with a disk that is assigned as a dedicated hot spare. The disk may have been removed. There may also be a bad or loose cable.
Action: Check if the disk is healthy and that it has not been removed. Check the cables. If necessary, replace the disk and reassign the hot spare.
|
Clear Alert: None
Related Alert Number: 2048
LRA Number: 2070
|
903
|
2202
|
A global hot spare has been removed.
|
OK / Normal / Informational
|
Cause: The controller is unable to communicate with a disk that is assigned as a global hot spare. The disk may have been removed. There may also be a bad or loose cable.
Action: Check if the disk is healthy and that it has not been removed. Check the cables. If necessary, replace the disk and reassign the hot spare.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2203
|
A dedicated hot spare failed.
|
Warning / Non-critical
|
Cause: The controller is unable to communicate with a disk that is assigned as a dedicated hot spare. The disk may have failed or been removed. There may also be a bad or loose cable.
Action: Check if the disk is healthy and that it has not been removed. Check the cables. If necessary, replace the disk and reassign the hot spare.
|
Clear Alert: None
Related Alert Number: 2048
LRA Number: 2070
|
903
|
2204
|
A dedicated hot spare has been removed.
|
OK / Normal / Informational
|
Cause: The controller is unable to communicate with a disk that is assigned as a dedicated hot spare. The disk may have been removed. There may also be a bad or loose cable.
Action: Check if the disk is healthy and that it has not been removed. Check the cables. If necessary, replace the disk and reassign the hot spare.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2205
|
A dedicated hot spare has been automatically unassigned.
|
OK / Normal / Informational
|
Cause: The hot spare is no longer required because the virtual disk it was assigned to has been deleted.
Action: None
|
Clear Alert: None
Related Alert Number: 2098, 2161, 2196
LRA Number: None
|
901
|
2206
|
The only hot spare available is a SATA disk. SATA disks cannot replace SAS disks.
|
Warning / Non-critical
|
Cause: The only physical disk available to be assigned as a hot spare is using SATA technology. The physical disks in the virtual disk are using SAS technology. Because of this difference in technology, the hot spare cannot rebuild data if one of the physical disks in the virtual disk fails.
Action: Add a SAS disk that is large enough to be used as the hot spare and assign it as a hot spare.
|
Clear Alert: None
Related Alert Number: None
LRA Number: 2070
|
903
|
2207
|
The only hot spare available is a SAS disk. SAS disks cannot replace SATA disks.
|
Warning / Non-critical
|
Cause: The only physical disk available to be assigned as a hot spare is using SAS technology. The physical disks in the virtual disk are using SATA technology. Because of this difference in technology, the hot spare cannot rebuild data if one of the physical disks in the virtual disk fails.
Action: Add a SATA disk that is large enough to be used as the hot spare and assign the new disk as a hot spare.
|
Clear Alert: None
Related Alert: None
LRA Number: 2070
|
903
|
2210
|
Battery requires reconditioning. Initiate the battery learn cycle.
|
Warning / Non-critical
|
Cause: Battery is in warn only mode and requires reconditioning.
Action: Initiate the battery learn cycle.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1153
|
2211
|
The physical disk is not supported.
|
Warning / Non-critical
|
Cause: The physical disk may not have a supported version of the firmware or the disk may not be supported by your service provider.
Action: If the disk is supported, update the firmware to a supported version. If the disk is not supported by your service provider, replace the disk with one that is supported.
|
Clear Alert: None
Related Alert: None
LRA Number: 2070
|
903
|
2212
|
The controller battery temperature is above normal.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2213
|
Recharge count maximum exceeded
|
Warning / Non-critical
|
Cause: The battery has been recharged more times than the battery recharge limit allows.
Action: Replace the battery pack.
|
Clear Alert: None
Related Alert: None
LRA Number: 2100
|
1153
|
2214
|
Battery charge in progress
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2215
|
Battery charge process interrupted
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2216
|
The battery learn mode has changed to auto.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2217
|
The battery learn mode has changed to warn.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2218
|
None of the Controller Property are set.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: You should change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2219
|
Abort Check Consistency on Error, Replace Member Operation, Auto Replace Member Operation on Predictive Failure and Loadbalance changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2220
|
Replace Member Operation, Auto Replace Member Operation on Predictive Failure and Loadbalance changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2221
|
Auto Replace Member Operation on Predictive Failure, Abort CC on Error and Loadbalance changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2222
|
Loadbalance and Auto Replace Member Operation on Predictive Failure changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2223
|
Abort Check Consistency on Error, Replace Member Operation and Loadbalance changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2224
|
Replace Member Operation and Loadbalance changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2225
|
Abort Check Consistency on Error and Load balance changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2226
|
Load balance changed
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2227
|
Abort Check Consistency on Error, Replace Member Operation and Auto Replace Member Operation on Predictive Failure changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2228
|
Replace Member Operation and Auto Replace Member Operation on Predictive Failure changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2229
|
Abort Check Consistency on Error and Auto Replace Member Operation on Predictive Failure changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2230
|
Auto Replace Member Operation on Predictive Failure changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2231
|
Replace Member Operation and and Abort Check Consistency on Error changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2232
|
The controller alarm is silenced.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2233
|
The Background initialization (BGI) rate has changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2234
|
The Patrol Read rate has changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2235
|
The Check Consistency rate has changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2236
|
Replace Member Operation modified.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2237
|
Abort Check Consistency on Error modified.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: Change at least one controller property and run the command again.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2238
|
The controller debug log file has been exported.
|
OK / Normal / Informational
|
Cause: The user has attempted to export the controller debug log. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2239
|
A foreign configuration has been cleared.
|
OK / Normal / Informational
|
Cause: The user has attempted to clear a foreign configuration. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2240
|
A foreign configuration has been imported.
|
OK / Normal / Informational
|
Cause: The user has attempted to import a foreign configuration. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2241
|
The Patrol Read mode has changed.
|
OK / Normal / Informational
|
Cause: The controller has changed the patrol read mode. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2242
|
The Patrol Read operation has started.
|
OK / Normal / Informational
|
Cause: The controller has started the Patrol Read operation. This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2243
Related Alert: None
LRA Number: None
|
751
|
2243
|
The Patrol Read operation has stopped.
|
OK / Normal / Informational
|
Cause: The controller has stopped the Patrol Read operation. This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2243 is a clear alert for alert 2242.
Related Alert: None
LRA Number: None
|
751
|
2244
|
A virtual disk blink has been initiated.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2245
|
A virtual disk blink has ceased.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2246
|
The controller battery is degraded.
|
Warning / Non-critical
|
Cause: The temperature of the the battery is high. This maybe due to the battery being charged.
Action: As the charge weakens, the charger should automatically recharge the battery. If the battery has reached its recharge limit, replace the battery pack. Monitor the battery to make sure that it recharges successfully.
|
Clear Alert: None
Related Alert: None
LRA Number: 2100
|
1153
|
2247
|
The controller battery is charging.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2358
Related Alert: None
LRA Number: None
|
1151
|
2248
|
The controller battery is executing a Learn cycle.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2249
|
The physical disk Clear operation has started.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2250
|
Redundant Path is broken
|
Warning /Non-critical
|
Cause: The redundant path is broken.
Action: Check the connection to the enclosure, which is degraded.
|
Clear Alert Number: 2370.
Related Alert Number: 2370.
LRA Number: None
|
751
|
2251
|
The physical disk blink has initiated.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2252
|
The physical disk blink has ceased.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2253
|
Redundant path restored
|
OK / Normal / Informational
|
Cause: This alert is provided for informational purposes.
None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2254
|
The Clear operation has cancelled.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2255
|
The physical disk has been started.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert Number: 2048, 2050, 2065, 2099, 2121, 2196, 2201, 2203
LRA Number: None
|
901
|
2257
|
Controller preserved cache is discarded
|
Warning /Non-critical
|
Cause: The controller cache is discarded by the user. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
753
|
2258
|
Controller has preserved cache
|
Warning /Non-critical
|
Cause: I/O interrupted for a virtual disk which is connected to the controller.
Action: Check for foreign configuration and import if any. Check for cable fault. Recover any virtual disk lost by the controller.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
753
|
2259
|
An enclosure blink operation has initiated.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Number: 2260
Related Alert: None
LRA Number: None
|
851
|
2260
|
An enclosure blink has ceased.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
851
|
2261
|
A global rescan has initiated.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2262
|
SMART thermal shutdown is enabled.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
101
|
2263
|
SMART thermal shutdown is disabled.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
101
|
2264
|
A device is missing.
|
Warning / Non-critical
|
Cause: The controller cannot communicate with a device. The device may be removed. There may also be a bad or loose cable.
Action: Check if the device is in and not removed. If it is in, check the cables. Also check the connection to the controller battery and the battery health. A battery with a weak or depleted charge may cause this alert.
|
Clear Alert: None
Related Alert: None
LRA Number: 2050, 2060, 2070, 2080, 2090, 2100
|
753 803 853 903 953 1003 1053 1103 1153 1203
|
2265
|
A device is in an unknown state.
|
Warning / Non-critical
|
Cause: The controller cannot communicate with a device. The state of the device cannot be determined. There may be a bad or loose cable. The system may also be experiencing problems with the application programming interface (API). There could also be a problem with the driver or firmware.
Action: Check the cables. Check if the controller has a supported version of the driver and firmware. You can download the current version of the driver and firmware from the support site. Rebooting the system may also resolve this problem.
|
Clear Alert: None
Related Alert Number: 2048, 2050
LRA Number: 2050, 2060, 2070, 2080, 2090, 2100
|
753 803 853 903 953 1003 1053 1103 1153 1203
|
2266
|
Controller log file entry: %1
|
OK / Normal / Informational
|
Cause: The %1 indicates a substitution variable. The text for this substitution variable is generated by the controller and is displayed with the alert in the alert log. This text can vary depending on the situation. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751, 801, 851, 901, 951, 1001, 1051, 1101, 1151, 1201
|
2267
|
The controller reconstruct rate has changed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2268
|
%1, Storage Management has lost communication with the controller. An immediate reboot is strongly recommended to avoid further problems. If the reboot does not restore communication, then contact technical support for more information.
|
Critical / Failure / Error
|
Cause: Storage Management has lost communication with a controller. This may occur if the controller driver or firmware is experiencing a problem. The %1 indicates a substitution variable. The text for this substitution variable is displayed with the alert in the alert log and can vary depending on the situation.
Action: Reboot the system. If the problem is not resolved, contact technical support. See your system documentation for information about contacting technical support by using telephone, fax, and Internet services.
|
Clear Alert: None
Related Alert: None
LRA Number: 2051
|
104
|
2269
|
The physical disk Clear operation has completed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2270
|
The physical disk Clear operation failed.
|
Critical / Failure / Error
|
Cause: A Clear task was being performed on a physical disk but the task was interrupted and did not complete successfully. The controller may have lost communication with the disk. The disk may have been removed or the cables may be loose or defective.
Action: Verify that the disk is present and not in a Failed state. Make sure the cables are attached securely. See the online help for more information on checking the cables. Restart the Clear task.
|
Clear Alert: None
Related Alert: None
LRA Number: 2071
|
904
|
2271
|
The Patrol Read encountered a media error.
|
OK / Normal / Informational
|
Cause: The Patrol Read task has encountered an error such as a bad disk block that cannot be remapped. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2272
|
Patrol Read found an uncorrectable media error.
|
Critical / Failure / Error
|
Cause: The Patrol Read task has encountered an error that cannot be corrected. There may be a bad disk block that cannot be remapped.
Action: Back up your data. If you are able to back up the data successfully, then fully initialize the disk and then restore from back up.
|
Clear Alert: None
Related Alert: None
LRA Number: 2071
|
904
|
2273
|
A block on the physical disk has been punctured by the controller.
|
Critical / Failure / Error
|
Cause: The controller encountered an unrecoverable medium error when attempting to read a block on the physical disk and marked that block as invalid. If the error was encountered on a source physical disk during a rebuild or reconfigure operation, it also punctures the corresponding block on the target physical disk. The invalid block is cleared during a write operation.
Action: Back up your data. If you are able to back up the data successfully, initialize the disk and restore from the back up.
|
Clear Alert: None
Related Alert: 2095, 2350
LRA Number: 2071
|
904
|
2274
|
The physical disk rebuild has resumed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2276
|
The dedicated hot spare is too small.
|
Warning / Non-critical
|
Cause: The dedicated hot spare is not large enough to protect all virtual disks that reside on the disk group.
Action: Assign a larger disk as the dedicated hot spare.
|
Clear Alert: None
Related Alert: None
LRA Number: 2070
|
903
|
2277
|
The global hot spare is too small.
|
Warning / Non-critical
|
Cause: The global hot spare is not large enough to protect all virtual disks that reside on the controller.
Action: Assign a larger disk as the global hot spare.
|
Clear Alert: None
Related Alert: None
LRA Number: 2070
|
903
|
2278
|
The controller battery charge level is below a normal threshold.
|
OK / Normal / Informational
|
Cause: The battery is discharging. A battery discharge is a normal activity during the battery Learn cycle. The battery Learn cycle recharges the battery. You should receive alert 2179 when the recharge occurs.
Action1: Check if the battery Learn cycle is in progress. The battery also displays the Learn state while the Learn cycle is in progress. Action2: If a Learn cycle is not in progress, replace the battery pack.
|
Clear Alert: None
Related Alert Number: 2199
LRA Number: None
|
1151
|
2279
|
The controller battery charge level is operating within normal limits.
|
OK / Normal / Informational
|
Cause: This alert indicates that the battery is recharging during the battery Learn cycle. This alert is provided for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2280
|
A disk media error has been corrected.
|
OK / Normal / Informational
|
Cause: A disk media error was detected while the controller was completing a background task. A bad disk block was identified. The disk block has been remapped.
Action: Consider replacing the disk. If you receive this alert frequently, be sure to replace the disk. You should also routinely back up your data.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2281
|
Virtual disk has inconsistent data.
|
OK / Normal / Informational
|
Cause: The virtual disk has inconsistent data. This may be caused when a power loss or system shutdown occurs while data is being written to the virtual disk. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert Number: 2127
LRA Number: None
|
1201
|
2282
|
Hot spare SMART polling failed.
|
Critical / Failure / Error
|
Cause: The controller firmware attempted a SMART polling on the hot spare but was unable to complete it. The controller has lost communication with the hot spare.
Action: Check the health of the disk assigned as a hot spare. You may need to replace the disk and reassign the hot spare. Make sure the cables are attached securely. See the Server Administrator Storage Management User's Guide, for more information on checking the cables.
|
Clear Alert: None
Related Alert: None
LRA Number: 2071
|
904
|
2283
|
A redundant path is broken.
|
Warning / Non-critical
|
Cause: The controller has two connectors that are connected to the same enclosure. The communication path on one connector has lost connection with the enclosure. The communication path on the other connector is reporting this loss.
Action: Make sure the cables are attached securely and both enclosure management modules (EMMs) are healthy. See the Cables Attached Correctly section for more information on checking the cables.
|
Clear Alert: 2284
Related Alert: None
LRA Number: 2070
|
903
|
2284
|
A redundant path has been restored.
|
OK / Normal / Informational
|
Cause: This alert is provided for informational purposes.
Action: None
|
Clear Alert: Alert 2284 is a clear alert for alert 2283.
Related Alert: None
LRA Number: 2071
|
901
|
2285
|
A disk media error was corrected during recovery.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2286
|
A Learn cycle start is pending while the battery charges.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2287
|
Protection policy has been changed.
|
OK / Normal / Informational
|
Cause: A new protection policy has been created/ existing protection policy has been modified.
Action: None
|
Clear Alert: None
Related Alert: 2384
LRA Number: None
|
101
|
2288
|
The patrol read has resumed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: None.
Related Alert: None
LRA Number: None
|
751
|
2289
|
Multi-bit ECC error on controller DIMM.
|
Critical / Failure / Error
|
Cause: An error involving multiple bits has been encountered during a read or write operation. The error correction algorithm recalculates parity data during read and write operations. If an error involves only a single bit, it may be possible for the error correction algorithm to correct the error and maintain parity data. An error involving multiple bits, however, usually indicates data loss. In some cases, if the multi-bit error occurs during a read operation, the data on the disk may be OK. If the multi-bit error occurs during a write operation, data loss has occurred.
Action: Replace the dual in-line memory module (DIMM). The DIMM is a part of the controller battery pack. See your hardware documentation for information on replacing the DIMM. You may need to restore data from backup.
|
Clear Alert: None
Related Alert: None
LRA Number: 2061
|
754
|
2290
|
Single-bit ECC error on controller DIMM.
|
Warning / Non-critical
|
Cause: An error involving a single bit has been encountered during a read or write operation. The error correction algorithm has corrected this error.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2291
|
An enclosure management module (EMM) has been discovered.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
851
|
2292
|
Communication with the enclosure has been lost.
|
Critical / Failure / Error
|
Cause: The controller has lost communication with an EMM. The cables may be loose or defective.
Action: Make sure the cables are attached securely. Reboot the system.
|
Clear Alert Number: 2162
Related Alert: None
LRA Number: 2091
|
854
|
2293
|
The EMM has failed.
|
Critical / Failure / Error
|
Cause: The failure may be caused by a loss of power to the EMM. The EMM self test may also have identified a failure. There could also be a firmware problem or a multi-bit error.
Action: Replace the EMM. See the hardware documentation for information on replacing the EMM.
|
Clear Alert: None
Related Alert: None
LRA Number: 2091
|
854
|
2294
|
A device has been inserted.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
851
|
2295
|
A device has been removed.
|
Critical / Failure / Error
|
Cause: A device has been removed and the system is no longer functioning in optimal condition.
Action: Replace the device.
|
Clear Alert: None
Related Alert: None
LRA Number: 2091
|
854
|
2296
|
An EMM has been inserted.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
951
|
2297
|
An EMM has been removed.
|
Critical / Failure / Error
|
Cause: An EMM has been removed.
Action: Reinsert the EMM. See the hardware documentation for information on replacing the EMM.
|
Clear Alert: None
Related Alert: None
LRA Number: 2091
|
854, 954
|
2298
|
The enclosure has a bad sensor %1.
|
Warning / Non-critical
|
Cause: The enclosure has a bad sensor. The enclosure sensors monitor the fan speeds, temperature probes, and so on. The %1indicates a substitution variable. The text for this substitution variable is displayed with the alerts in the alert log and can vary depending on the situation.
Action: See the hardware documentation for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2090
|
853
|
2299
|
Bad PHY %1
|
Critical / Failure / Error
|
Cause: There is a problem with a physical connection or PHY. The %1 indicates a substitution variable. The text for this substitution variable is displayed with the alert in the alert log and can vary depending on the situation.
Action: Contact your technical support.
|
Clear Alert: None
Related Alert: None
LRA Number: 2091
|
854
|
2300
|
The enclosure is unstable.
|
Critical / Failure / Error
|
Cause: The controller is not receiving a consistent response from the enclosure. There could be a firmware problem or an invalid cabling configuration. If the cables are too long, they degrade the signal.
Action: Power down all enclosures attached to the system and reboot the system. If the problem persists, upgrade the firmware to the latest supported version. You can download the most current version of the driver and firmware from the support site. Make sure the cable configuration is valid. See the hardware documentation for valid cabling configurations.
|
Clear Alert: None
Related Alert: None
LRA Number: 2091
|
854
|
2301
|
The enclosure has a hardware error.
|
Critical / Failure / Error
|
Cause: The enclosure or an enclosure component is in a Failed or Degraded state.
Action: Check the health of the enclosure and its components. Replace any hardware that is in a Failed state. See the hardware documentation for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2091
|
854
|
2302
|
The enclosure is not responding.
|
Critical / Failure / Error
|
Cause: The enclosure or an enclosure component is in a Failed or Degraded state.
Action: Check the health of the enclosure and its components. Replace any hardware that is in a Failed state. See the hardware documentation for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2091
|
854
|
2303
|
The enclosure cannot support both SAS and SATA physical disks. Physical disks may be disabled.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
851
|
2304
|
An attempt to hot plug an EMM has been detected. This type of hot plug is not supported.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert Number: 2211
LRA Number: None
|
751
|
2305
|
The physical disk is too small to be used for a rebuild.
|
Warning / Non-critical
|
Cause: The physical disk is too small to rebuild the data.
Action: Remove the physical disk and insert a new physical disk that is the same size or larger than the disk that is being rebuilt. The new physical disk must also use the same technology (for example, SAS or SATA) as the disk being rebuilt. If the rebuild does not start automatically after you have inserted a suitable physical disk, then run the Rebuild task. See the Server Administrator Storage Management User's Guide for more information.
|
Clear Alert: None
Related Alert Number: 2326
LRA Number: 2070
|
903
|
2306
|
Bad block table is 80% full.
|
Warning / Non-critical
|
Cause: The bad block table is used for remapping bad disk blocks. This table fills, as bad disk blocks are remapped. When the table is full, bad disk blocks can no longer be remapped, and disk errors can no longer be corrected. At this point, data loss can occur. The bad block table is now 80% full.
Action: Back up your data. Replace the disk generating this alert and restore from back up.
|
Clear Alert: None
Related Alert Number: 2307
LRA Number: 2070
|
903
|
2307
|
Bad block table is full. Unable to log block %1
|
Critical / Failure / Error
|
Cause: The bad block table is used for remapping bad disk blocks. This table fills, as bad disk blocks are remapped. When the table is full, bad disk blocks can no longer be remapped and disk errors can no longer be corrected. At this point, data loss can occur. The %1 indicates a substitution variable. The text for this substitution variable is displayed with the alert in the alert log and can vary depending on the situation.
Action: Replace the disk generating this alert. If necessary, restore your data from backup.
|
Clear Alert: None
Related Alert Number: 2048
LRA Number: 2071
|
904
|
2309
|
A physical disk is incompatible.
|
Warning / Non-critical
|
Cause: You have attempted to replace a disk with another disk that is using an incompatible technology. For example, you may have replaced one side of a mirror with a SAS disk when the other side of the mirror is using SATA technology.
Action: See the hardware documentation for information on replacing disks.
|
Clear Alert: None
Related Alert: None
LRA Number: 2070
|
903
|
2310
|
A virtual disk is permanently degraded.
|
Critical / Failure / Error
|
Cause: A redundant virtual disk has lost redundancy. This may occur when the virtual disk suffers the failure of multiple physical disks. In this case, both the source physical disk and the target disk with redundant data have failed. A rebuild is not possible because there is no redundancy.
Action: Replace the failed disks and restore from backup.
|
Clear Alert: None
Related Alert: None
LRA Number: 2081
|
1204
|
2311
|
The firmware on the EMMs is not the same version. EMM0 %1 EMM1 %2
|
Warning / Non-critical
|
Cause: The firmware on the EMM modules is not the same version. It is required that both modules have the same version of the firmware. This alert may be caused if you attempt to insert an EMM module that has a different firmware version than an existing module. The %1 and %2 indicate a substitution variable. The text for these substitution variables is displayed with the alert in the alert log and can vary depending on the situation.
Action: Upgrade to the same version of the firmware on both EMM modules.
|
Clear Alert: None
Related Alert: None
LRA Number: 2090
|
853
|
2312
|
A power supply in the enclosure has an AC failure.
|
Warning / Non-critical
|
Cause: The power supply has an AC failure.
Action: Replace the power supply.
|
Clear Alert Number: 2325
Related Alert Number: 2122, 2324.
LRA Number: 2090
|
1003
|
2313
|
A power supply in the enclosure has a DC failure.
|
Warning / Non-critical
|
Cause: The power supply has a DC failure.
Action: Replace the power supply.
|
Clear Alert Number: 2323
Related Alert Number: 2122, 2322.
LRA Number: 2090
|
1003
|
2314
|
The initialization sequence of SAS components failed during system startup. SAS management and monitoring is not possible.
|
Critical / Failure / Error
|
Cause: Storage Management is unable to monitor or manage SAS devices.
Action: Reboot the system. If problem persists, make sure you have supported versions of the drivers and firmware. Also, you may need to reinstall Storage Management or Server Administrator because of some missing installation components.
|
Clear Alert: None
Related Alert: None
LRA Number: 2051
|
104
|
2315
|
Diagnostic message %1
|
OK / Normal / Informational
|
Cause: The %1 indicates a substitution variable. The text for this substitution variable is generated by the utility that ran the diagnostics and is displayed with the alert in the alert log. This text can vary depending on the situation. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2316
|
Diagnostic message %1
|
Critical / Failure / Error
|
Cause: A diagnostics test failed. The %1 indicates a substitution variable. The text for this substitution variable is generated by the utility that ran the diagnostics and is displayed with the alert in the alert log. This text can vary depending on the situation.
Action: See the documentation for the utility that ran the diagnostics for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2061
|
754
|
2318
|
Problems with the battery or the battery charger have been detected. The battery health is poor.
|
Warning / Non-critical
|
Cause: The battery or the battery charger is not functioning properly.
Action: Replace the battery pack.
|
Clear Alert: None
Related Alert Number: 2188
LRA Number: 2100
|
1153
|
2319
|
Single-bit ECC error. The DIMM is degrading.
|
Warning / Non-critical
|
Cause: The DIMM is beginning to malfunction.
Action: Replace the DIMM to avoid data loss or data corruption. The DIMM is a part of the controller battery pack. See your hardware documentation for information on replacing the DIMM or contact technical support.
|
Clear Alert: None
Related Alert Number: 2320
LRA Number: 2060
|
753
|
2320
|
Single-bit ECC error. The DIMM is critically degraded.
|
Critical / Failure / Error
|
Cause: The DIMM is malfunctioning. Data loss or data corruption may be imminent.
Action: Replace the DIMM immediately to avoid data loss or data corruption. The DIMM is a part of the controller battery pack. See your hardware documentation for information on replacing the DIMM or contact technical support.
|
Clear Alert: None
Related Alert Number: 2321
LRA Number: 2061
|
754
|
2321
|
Single-bit ECC error. The DIMM is critically nonfunctional. There is no further reporting.
|
Critical / Failure / Error
|
Cause: The DIMM is malfunctioning. Data loss or data corruption is imminent. No further alerts are generated.
Action: Replace the DIMM immediately. The DIMM is a part of the controller battery pack. See your hardware documentation for information on replacing the DIMM.
|
Clear Alert: None
Related Alert: None
LRA Number: 2061
|
754
|
2322
|
The DC power supply is switched off.
|
Critical / Failure / Error
|
Cause: The power supply unit is switched off. Either a user switched off the power supply unit or it is defective.
Action: Check if the power switch is turned off. If it is turned off, turn it on. If the problem persists, check if the power cord is attached and functional. If the problem is still not corrected or if the power switch is already turned on, replace the power supply unit.
|
Clear Alert Number: 2323
Related Alert: None
LRA Number: 2091
|
1004
|
2323
|
The power supply is switched on.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2323 is a clear alert for alerts 2313 and 2322.
Related Alert: None
LRA Number: None
|
1001
|
2324
|
The AC power supply cable has been removed.
|
Critical / Failure / Error
|
Cause: The power cable may be pulled out or removed. The power cable may also have overheated and become warped and nonfunctional.
Action: Replace the power cable.
|
Clear Alert Number: 2325
Related Alert: None
LRA Number: 2091
|
1004
|
2325
|
The power supply cable has been inserted.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert Status: Alert 2325 is a clear alert for alerts 2324 and 2312.
Related Alert: None
LRA Number: None
|
1001
|
2326
|
A foreign configuration has been detected.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes. The controller has physical disks that were moved from another controller. These physical disks contain virtual disks that were created on the other controller. See the Import Foreign Configuration and Clear Foreign Configuration section in the Server Administrator Storage Management User's Guide for more information.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2327
|
The NVRAM has corrupted data. The controller is reinitializing the NVRAM.
|
Warning / Non-critical
|
Cause: The nonvolatile random access memory (NVRAM) is corrupt. This may occur after a power surge, a battery failure, or for other reasons. The controller is reinitializing the NVRAM. The controller properties reset to the default settings after the reinitialization is complete.
None The controller is taking the required corrective action. If this alert is generated often (such as during each reboot), replace the controller.
|
Clear Alert: None
Related Alert Number: 2266
LRA Number: 2060
|
753
|
2328
|
The NVRAM has corrupt data.
|
Warning / Non-critical
|
Cause: The NVRAM has corrupt data. The controller is unable to correct the situation.
Action: Replace the controller.
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2329
|
SAS port report: %1
|
Warning / Non-critical
|
Cause: The text for this alert is generated by the controller and can vary depending on the situation. The %1 indicates a substitution variable. The text for this substitution variable is generated by the controller and is displayed with the alert in the alert log. This text can vary depending on the situation.
Action: Run the PHY integrity test diagnostic. Make sure the cables are attached securely. If the problem persists, replace the cable with a valid cable according to SAS specifications. If the problem still persists, you may need to replace some devices such as the controller or EMM. See the hardware documentation for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2330
|
SAS port report: %1
|
OK / Normal / Informational
|
Cause: The %1 indicates a substitution variable. The text for this substitution variable is generated by the controller and is displayed with the alert in the alert log. This text can vary depending on the situation. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2331
|
A bad disk block has been reassigned.
|
OK / Normal / Informational
|
Cause: The disk has a bad block. Data has been readdressed to another disk block and no data loss has occurred.
Action: Monitor the disk for other alerts or indications of poor health. For example, you may receive alert 2306. Replace the disk if you suspect there is a problem.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2332
|
A controller hot plug has been detected.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2334
|
Controller event log: %1
|
OK / Normal / Informational
|
Cause: The %1 indicates a substitution variable. The text for this substitution variable is generated by the controller and is displayed with the alert in the alert log. This text is from events in the controller event log that were generated while Storage Management was not running. This text can vary depending on the situation. This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2335
|
Controller event log: %1
|
Warning / Non-critical
|
Cause: The %1 indicates a substitution variable. The text for this substitution variable is generated by the controller and is displayed with the alert in the alert log. This text is from events in the controller event log that were generated while Storage Management was not running. This text can vary depending on the situation.
Action: If there is a problem, review the controller event log and the Server Administrator alert log for significant events or alerts that may assist in diagnosing the problem. Check the health of the storage components. See the hardware documentation for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2336
|
Controller event log: %1
|
Critical / Failure / Error
|
Cause: The %1 indicates a substitution variable. The text for this substitution variable is generated by the controller and is displayed with the alert in the alert log. This text is from events in the controller event log that were generated while Storage Management was not running. This text can vary depending on the situation.
Action: See the hardware documentation for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2061
|
754
|
2337
|
The controller is unable to recover cached data from the battery backup unit (BBU).
|
Critical / Failure / Error
|
Cause: The controller was unable to recover data from the cache. This may occur when the system is without power for an extended period of time when the battery is discharged.
Action: Check if the battery is charged and in good health. When the battery charge is unacceptably low, it cannot maintain cached data. Check if the battery has reached its recharge limit. The battery may need to be recharged or replaced.
|
Clear Alert: None
Related Alert: None
LRA Number: 2101
|
1154
|
2338
|
The controller has recovered cached data from the BBU.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2339
|
The factory default settings have been restored.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2340
|
The BGI completed with uncorrectable errors.
|
Critical / Failure / Error
|
Cause: The BGI task encountered errors that cannot be corrected. The virtual disk contains physical disks that have unusable disk space or disk errors that cannot be corrected.
Action: Replace the physical disk that contains the disk errors. Review other alert messages to identify the physical disk that has errors. If the virtual disk is redundant, you can replace the physical disk and continue using the virtual disk. If the virtual disk is non-redundant, you may need to recreate the virtual disk after replacing the physical disk. After replacing the physical disk, run Check Consistency to check the data.
|
Clear Alert: None
Related Alert: None
LRA Number: 2081
|
1204
|
2341
|
The Check Consistency made corrections and completed.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2342
|
The Check Consistency found inconsistent parity data. Data redundancy may be lost.
|
Warning / Non-critical
|
Cause: The data on a source disk and the redundant data on a target disk is inconsistent.
Action: Restart the Check Consistency task. If you receive this alert again, check the health of the physical disks included in the virtual disk. Review the alert messages for significant alerts related to the physical disks. If you suspect that a physical disk has a problem, replace it and restore from backup.
|
Clear Alert: None
Related Alert Number: 2341, 2343
LRA Number: 2080
|
1203
|
2343
|
The Check Consistency logging of inconsistent parity data is disabled.
|
Warning / Non-critical
|
Cause: The Check Consistency can no longer report errors in the parity data.
Action: See the hardware documentation for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2080
|
1203
|
2344
|
The virtual disk initialization terminated.
|
Warning / Non-critical
|
Cause: A user has cancelled the virtual disk initialization.
Action: Restart the initialization.
|
Clear Alert: None
Related Alert: None
LRA Number: 2080
|
1203
|
2345
|
The virtual disk initialization failed.
|
Critical / Failure / Error
|
Cause: The controller cannot communicate with attached devices. A disk may be removed or contain errors. Cables may also be loose or defective.
Action: Verify the health of attached devices. Review the Alert Log for significant events. Make sure the cables are attached securely. See the Cables Attached Correctly section for more information on checking the cables.
|
Clear Alert: None
Related Alert: None
LRA Number: 2081
|
1204
|
2346
|
Error occurred: %1
|
Warning / Non-critical
|
Cause: A physical device may have an error. The %1 indicates a substitution variable. The text for this substitution variable is generated by the firmware and is displayed with the alert in the alert log. This text can vary depending on the situation.
Action: Verify the health of attached devices. Review the alert log for significant events. Run the PHY integrity diagnostic tests. You may need to replace faulty hardware. Make sure the cables are attached securely. See the hardware documentation for more information.
|
Clear Alert: None
Related Alert Number: 2048, 2050, 2056, 2057, 2076, 2079, 2081, 2083, 2095, 2129, 2201, 2203, 2270, 2282, 2369
LRA Number: 2070
|
903
|
2347
|
The rebuild failed due to errors on the source physical disk.
|
Critical / Failure / Error
|
Hardware RAID:
Cause: You are attempting to rebuild data that resides on a defective disk.
Action: Replace the source disk and restore from backup.
Software RAID:
•
|
Perform a backup with the Verify option.
|
•
|
If the file backup fails, try to restore the failed file from a previous backup.
|
•
|
When the backup with the Verify option is complete without any errors, delete the Virtual Disk.
|
•
|
Recreate a new Virtual Disk with new drives.
|
•
|
Restore the data from backup.
|
|
Clear Alert: None
Related Alert Number: 2195, 2346
LRA Number: 2071
|
904
|
2348
|
The rebuild failed due to errors on the target physical disk.
|
Critical / Failure / Error
|
Cause: You are attempting to rebuild data on a disk that is defective.
Action: Replace the target disk. If a rebuild does not automatically start after replacing the disk, initiate the Rebuild task. You may need to assign the new disk as a hot spare to initiate the rebuild.
|
Clear Alert: None
Related Alert Number: 2195, 2346
LRA Number: 2071
|
904
|
2349
|
A bad disk block could not be reassigned during a write operation.
|
Critical / Failure / Error
|
Cause: A write operation could not complete because the disk contains bad disk blocks that could not be reassigned. Data loss may have occurred and data redundancy may also be lost.
Action: Replace the disk.
|
Clear Alert: None
Related Alert Number: 2346
LRA Number: 2071
|
904
|
2350
|
There was an unrecoverable disk media error during the rebuild or recovery operation.
|
Critical / Failure / Error
|
Cause: The rebuild or recovery operation encountered an unrecoverable disk media error.
Action: Replace the disk.
|
Clear Alert: None
Related Alert Number: 2095, 2273
LRA Number: 2071
|
904
|
2351
|
A physical disk is marked as missing.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert Number: 2352
Related Alert: None
LRA Number: None
|
901
|
2352
|
A physical disk that was marked as missing has been replaced.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert Status: Alert 2352 is a clear alert for alert 2351.
Related Alert: None
LRA Number: None
|
901
|
2353
|
The enclosure temperature has returned to normal.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert Status: Alert 2353 is a clear alert for alerts 2100 and 2101.
Related Alert: None
LRA Number: None
|
1051
|
2354
|
Enclosure firmware download in progress.
|
OK / Normal / Informational
|
Cause: This alert is provided for informational purposes.
Action: None
|
Clear Alert Status: None
Related Alert: None
LRA Number: None
|
851
|
2355
|
Enclosure firmware download failed.
|
Warning / Non-critical
|
Cause: The system was unable to download firmware to the enclosure. The controller may have lost communication with the enclosure. There may have been problems with the data transfer or the download media may be corrupt.
Action: Attempt to download the enclosure firmware again. If problems continue, verify that the controller can communicate with the enclosure. Make sure that the enclosure is powered on. Check the cables. See the Cables Attached Correctly section for more information on checking the cables. Verify the health of the enclosure and its components. To verify the health of the enclosure, select the enclosure object in the tree view. The Health subtab displays a red X or yellow exclamation point for enclosure components that are failed or degraded.
|
Clear Alert Status: None
Related Alert: None
LRA Number: 2090
|
853
|
2356
|
SAS SMP communications error %1
|
Critical / Failure / Error
|
Cause: The text for this alert is generated by the firmware and can vary depending on the situation. The reference to SMP in this text refers to SAS Management Protocol.
Action: There may be a SAS topology error. See the hardware documentation for information on correct SAS topology configurations. There may be problems with the cables such as a loose connection or an invalid cabling configuration. See the Cables Attached Correctly section for more information on checking the cables. See the hardware documentation for information on correct cabling configurations. Verify that the firmware is a supported version.
|
Clear Alert: None
Related Alert: None
LRA Number: 2061
|
754
|
2357
|
SAS expander error: %1
|
Critical / Failure / Error
|
Cause: The %1 indicates a substitution variable. The text for this substitution variable is generated by the firmware and is displayed with the alert in the alert log. This text can vary depending on the situation.
Action: There may be a problem with the enclosure. Check the health of the enclosure and its components by selecting the enclosure object in the tree view. The Health subtab displays a red X or yellow exclamation point for enclosure components that are Failed or Degraded. See the enclosure documentation for more information.
|
Clear Alert: None
Related Alert: None
LRA Number: 2061
|
754
|
2358
|
The battery charge cycle is complete.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1151
|
2359
|
Disk found is not supplied by an authorized hardware provider
|
Warning / Non-critical
|
Cause: The physical disk does not comply with the standards set and is not supported.
Action: Replace the physical disk with a physical disk that is supported.
|
Clear Alert: None
Related Alert: None
LRA Number: 2070
|
903
|
2360
|
A user has discarded data from the controller cache.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2361
|
Physical disk(s) that are part of a virtual disk have been removed while the system was shut down. This removal was discovered during system startup.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2362
|
Physical disk(s) have been removed from a virtual disk. The virtual disk is in Failed state during the next system reboot.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2364
|
All virtual disks are missing from the controller. This situation was discovered during system startup.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2366
|
Dedicated spare imported as global due to missing arrays
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2367
|
Rebuild is not possible because mixing of different media type (SSD/HDD) and bus protocols (SATA/SAS) is not supported on the same virtual disk.
|
Warning / Non-critical
|
Cause: The physical disk is using an incompatible technology.
Action: All physical disks in the virtual disk must use the same technology. You cannot use both SAS and SATA physical disks in the same virtual disk. Remove the physical disk and insert a new physical disk that uses the correct technology. If the rebuild does not start automatically after you have inserted a suitable physical disk, then run the Rebuild task.
|
Clear Alert: None
Related Alert Number: 2326
LRA Number: 2070
|
903
|
2368
|
The SCSI Enclosure Processor (SEP) has been rebooted as part of the firmware download operation and is unavailable until the operation completes.
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert Number: 2049, 2052, 2162, 2292
LRA Number: None
|
851
|
2369
|
Virtual Disk Redundancy has been degraded.
|
OK / Normal / Informational
|
Cause: A physical disk in a RAID 6 virtual disk has either failed or been removed.
Action: Replace the missing or failed physical disk.
|
Clear Alert Number: 2121
Related Alert Number: 2048, 2049, 2050, 2076, 2346
LRA Number: None
|
1201
|
2370
|
Redundant Path View cleared
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2371
|
Attempted import of Unsupported Virtual Disk type RAID%1
|
OK / Normal / Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2372
|
Attempted import of Virtual Disk exceeding the limit supported on the controller.
|
OK / Normal / Informational
|
Cause: This alert is provided for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2373
|
Attempted import of unsupported Virtual Disk type RAID %1
|
OK / Normal / Informational
|
Cause: This alert is provided for informational purposes. User is attempting to import a foreign virtual disk with unsupported RAID level on the controller.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2374
|
Attempted import of Virtual Disk with missing span
|
OK / Normal / Informational
|
Cause: This alert is provided for informational purposes and is displayed when you attempt to import a foreign virtual disk with a missing span.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2375
|
Attempted import of Virtual Disk with missing physical disk
|
OK / Normal / Informational
|
Cause: User is attempting to import a foreign virtual disk with a missing physical disk. This alert is provided for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2376
|
Attempted import of Virtual Disk with stale physical disk
|
OK / Normal / Informational
|
Cause: User is attempting to import a foreign virtual disk with a stale physical disk. This alert is provided for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2377
|
Attempted import of an orphan drive
|
OK / Normal / Informational
|
Cause: User is attempting to import an orphan drive. This alert is provided for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2378
|
Attempted import of an incompatible physical drive
|
OK / Normal / Informational
|
Cause: User is attempting to import an incompatible physical drive. This alert is provided for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2379
|
An overflow of the foreign configuration has occurred. You can import the foreign configuration in multiple attempts
|
OK / Normal / Informational
|
Cause: This alert is provided for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2380
|
Foreign configuration has been partially imported. Some configuration failed to import.
|
OK / Normal / Informational
|
Cause: This alert is provided for informational purposes.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2381
|
Controller preserved cache is recovered.
|
OK / Normal / Informational
|
Cause: This alert is provided for informational purposes.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2382
|
An un-supported configuration was detected. The controller does not support physical disks of type SSD:
<Physical DiskID>, <controller-ID>, <connector- ID>
|
Warning / Non-critical
|
Cause: A physical disk of media type SSD is attached to a controller that does not support SSD disks.
Action: Replace the unsupported physical disk with a physical disk of media type HDD.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
903
|
2383
|
The Information level set for the hot spare protection policy is violated for the Virtual Disk.
|
OK / Normal / Informational
|
Cause: The number of physical disks you specified for the hot spare protection policy is violated.
Action: Reassign the number of hot spares as specified in the protection policy for that RAID level.
|
Clear Alert: 2195
Related Alert: None
LRA Number: None
|
1201
|
2384
|
The Warning level set for the hot spare protection policy is violated for the Virtual Disk.
|
Warning / Non-critical
|
Cause: The number of physical disks you specified for the hot spare protection policy is violated.
Action: Reassign the number of hot spares as specified in the protection policy for that RAID level.
|
Clear Alert: 2195
Related Alert: None
LRA Number: None
|
1203
|
2385
|
The Critical level set for the hot spare protection policy is violated for the Virtual Disk.
|
Critical / Failure / Error
|
Cause: The number of physical disks you specified for the hot spare protection policy is violated.
Action: Reassign the number of hot spares as specified in the protection policy for that RAID level.
|
Clear Alert: 2195
Related Alert: None
LRA Number: None
|
1204
|
2386
|
The drive could not be assigned as a Dedicated Hot Spare.
|
Warning / Non-critical
|
Cause: The assignment of a Dedicated Hot Spare fails as the disk is invalid.
Action: None
|
Clear Alert: 2195
Related Alert: None
LRA Number: None
|
901
|
2387
|
A virtual disk bad block medium error is detected.
|
Critical / Failure / Error
|
Cause: Virtual disk bad blocks are due to presence of unrecoverable bad blocks on one or more member physical disks.
Action:
1
|
Perform a backup of the virtual disk with the Verify option selected. One of the following can occur:
|
•
|
Backup operation fails. In this case, restore the file from a previous backup. After restoring the file, run Patrol Read and check for bad blocks. If more bad blocks exist, proceed to step 2.
|
•
|
Backup operation completes without error. This indicates that there are no bad blocks on your virtual disk.
|
•
|
Backup operation displays bad blocks. This indicates that the bad blocks are located in a non-data area. Proceed to step 2.
|
2
|
To clear these bad blocks, execute the Clear Virtual Disk Bad Blocks task.
|
3
|
Run Patrol Read to ensure no new bad blocks are found.
|
|
Clear Alert: None
Related Alert: None
LRA Number: 2081
|
1204
|
2388
|
The Controller Encryption Key is destroyed.
|
OK / Normal / Informational
|
Cause: The Controller Encryption Key is destroyed.
Action: None.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2389
|
The virtual disk bad block medium error is cleared.
|
OK / Normal / Informational
|
Cause: Virtual disk bad blocks are cleared.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2390
|
The Instant Encrypt Erase operation is performed on the physical disk.
|
OK / Normal / Informational
|
Cause: Instant Encrypt Erase operation is successful on Self Encryption Disks (SEDs.)
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2392
|
The drive Encryption Key is invalid.
|
Warning / Non-critical
|
Cause: The controller failed to verify the specified Passphrase.
Action: Enter a correct Passphrase.
|
Clear Alert: None
Related Alert: None
LRA Number: 2060
|
753
|
2393
|
The virtual disk is encrypted.
|
OK / Normal / Informational
|
Cause: The Encrypted virtual disk operation on normal virtual disk (created using Self-encrypting disks only) is successful.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2394
|
Persistent Hot Spare is enabled.
|
OK / Normal / Informational
|
Cause: The Persistent Hot Spare option is enabled.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2395
|
Persistent Hot Spare is disabled.
|
OK / Normal / Informational
|
Cause: The Persistent Hot Spare option is disabled.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2396
|
The Check Consistency detected uncorrectable multiple medium errors
|
Critical / Failure / Error
|
Cause: The Check Consistency task detects uncorrectable multiple errors.
Action: Replace the failed physical disk. You can identify the failed disk by locating the disk that has a red "X" for its status. Rebuild the physical disk. When finished, restart the check consistency operation.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1204
|
2397
|
The Check Consistency completed with uncorrectable errors
|
Critical / Failure / Error
|
Cause: The Check Consistency task detected uncorrectable multiple errors.
Action: Replace the failed physical disk. You can identify the failed disk by locating the disk that has a red "X" for its status. Rebuild the physical disk. When finished, restart the check consistency operation.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1204
|
2398
|
The Manage Physical Disk Power property(s) changed
|
OK / Normal / Informational
|
Cause: The Manage Physical Disk Power properties are changed.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
751
|
2399
|
The Physical Disk Power status changed from 1% to 2%
|
OK / Normal / Informational
|
Cause: The physical disk power status is changed from one state to another. A physical disk can have the following power statuses: spun down, transition, and spun up.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2400
|
Physical disk configuration data updated as it was stale.
|
Warning / Non-critical
|
Cause: The physical disk configuration data is updated because it was outdated.
Action: None
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
901
|
2401
|
Configuration command could not be committed to disk. Configuration has to be re applied.
|
Failure / Error
|
Cause: The virtual disk configuration command did not succeed.
Action: Check for the recent configuration that has not taken effect. Re-apply the configuration.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
754
|
2402
|
Changing the Physical Disk Power status from 1% to 2% failed.
|
Failure / Error
|
Cause: When changing the Physical Disk Power status fails.
Action: Replace the physical disk.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
904
|
2403
|
Virtual Disk is available
|
OK / Normal / Informational
|
Cause: The operating system detects the newly created virtual disk.
Action: None
NOTE: This alert also appears when a CacheCade is created but is not available for the operating system (as it is a CacheCade and not a Virtual Disk).
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2404
|
Virtual Disk is not available
|
OK / Normal / Informational
|
Cause: The operating system does not detect the newly created virtual disk.
Action: Wait for some time.
|
Clear Alert: None
Related Alert: None
LRA Number: None
|
1201
|
2405
|
Command timeout on physical disk
|
Informational
|
Cause: The spundown physical disks take more time than the timeout period and the configuration commands are timed out.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2407
|
Controller Encryption mode is enabled in LKM
|
Informational
|
Cause: The Local Key Management (LKM) encryption mode is enabled.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
751
|
2411
|
Controller LKM Encryption key is changed
|
Informational
|
Cause: Using Manage Encryption Key operations, encryption key is changed.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
751
|
2412
|
Controller CacheCade is resized
|
Informational
|
Cause: This alert is provided for informational purposes.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1201
|
2413
|
Controller CacheCade is created
|
Informational
|
Cause: This alert is provided for informational purposes.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1201
|
2414
|
Controller CacheCade is deleted
|
Informational
|
Cause: This alert is provided for informational purposes.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1201
|
2415
|
Controller battery is discharging
|
Informational
|
Cause: The battery learn cycle has started.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1151
|
2416
|
Disk medium error detected
|
Warning / Non-critical
|
Cause: A part of the physical disk is damaged.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
903
|
2417
|
There is an unrecoverable medium error detected on virtual disk
|
Critical / Failure / Error
|
Cause: Unrecoverable medium error found on one or more member physical disks of a virtual disk.
Action: Perform a backup of the virtual disk with the Verify option selected. If the Backup operation is successful, it indicates that the un-recoverable medium did not affect user data.
If the Backup operation fails, restore the file from a previous backup. After restoring the file, run check consistency operation:
•
|
If the consistency check is successful, no further action is required.
|
•
|
If the consistency check finds and un-recoverable medium error, it means that the medium error is located in non-user data. No further action is required as, writing data to the location of the medium error fixes the problem.
|
NOTE: If the unrecoverable medium error has not been corrected, it may be reported again by the system. This error can be fixed by writing data on the affected area or deleting and recreating the Virtual Disk as demonstrated in the following procedure.
1
|
Back up the data.
|
2
|
Delete the Virtual Disk.
|
3
|
Recreate the Virtual Disk using the same parameters like size, RAID level, disks, etc.
|
4
|
Restore data.
|
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1204
|
2418
|
Disk medium error on virtual disk has been corrected
|
Informational
|
Cause: This alert is for informational purposes.
Action: None.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1201
|
2425
|
State change on Physical disk from READY to Non-RAID.
|
Informational
|
Cause: User triggered action.
Action: Configure the drive to be non-raid using CLI/GUI.
|
Clear Alert: None.
Related Alert: None
LRA Number:
|
901
|
2426
|
State change on Physical disk from Non-RAID to READY.
|
Informational
|
Cause: User triggered action.
Action: Configure the drive to be ready using CLI/GUI.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2429
|
Drive Prepared for Removal.
|
Informational
|
Cause: User triggered action.
Action: Execute "Prepare to Remove" task from UI in a PCIeSSD setup
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2430
|
Physical Device Log exported.
|
Informational
|
Cause: User triggered action.
Action: Execute export log for physical device
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2431
|
Physical Device Full Initialization completed.
|
Informational
|
Cause: User triggered task.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2432
|
The PCIeSSD device was found to be in security locked state. Full initialization has to be done on the security locked drive to recover the drive in usable state.
|
Warning
|
Cause: Last full initialization was stopped for some reason and hence the device is in security locked state.
Action: Run full initialization to recover the device.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
902
|
2433
|
Physical Device is at %1% of warranted device wear-out limit.
|
Informational
|
Cause: User triggered task.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2434
|
Physical Device has reached or exceeded its warranted device wear-out limit.
|
Warning
|
Cause: User triggered task.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
903
|
2435
|
Physical Device is approaching read-only mode.
|
Informational
|
Cause: User triggered task.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2436
|
Physical Device is in read-only mode.
|
Warning
|
Cause: User triggered task.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
903
|
2437
|
The physical device blink has initiated.
|
Informational
|
Cause: User triggered task.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2438
|
The physical device blink has ceased.
|
Informational
|
Cause: User triggered task.
Action: None
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2699
|
Connection to CFM lost! : FluidCache
|
Error
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1604
|
2700
|
The following journal mirror is available. %1
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1601
|
2701
|
The following journal mirror is being replaced.(wwn) %1 : FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1601
|
2702
|
The following journal mirror has failed.(wwn) %1 : FluidCache
|
Warning
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1603
|
2703
|
There are not enough journal mirrors available to operate. : FluidCache
|
Error
|
To resolve the issue, you must ensure that there are at least two journal mirrors that are accessible. You must activate either one or more failed cache devices or use the fldc_restore utility to rebuild the node.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1604
|
2704
|
The cluster ID in the journal does not match the cluster ID in the configuration file. : FluidCache
|
Error
|
Service is required. Contact Dell Technical Support.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1604
|
2705
|
The journal could not be read/written. : FluidCache
|
Error
|
Service is required. Contact Dell Technical Support.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1604
|
2874
|
The following Cache Device has no associated server in the configuration: %1 : FluidCache
|
Warning
|
There is a cache device specified in the configuration with no associated cache server configured.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
903
|
2875
|
The following Disk is beginning flushing.(wwn) %1 (path) %2 : FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2876
|
The following Disk has finished flushing.(wwn) %1 (path) %2 : FluidCacheg.
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2900
|
The following cache device has failed.(wwn) %1 (path) %2 : FluidCache
|
Error
|
Replace the failed device.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
904
|
2901
|
The following storage device is either inaccessible or failed.(wwn) %1 (path) %2 : FluidCache
|
Error
|
If the device is inaccessible, restore connectivity. If the device has failed, replace it.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1204, 1504
|
2902
|
The following storage device has had transient failures.(wwn) %1 (path) %2 : FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1201, 1501
|
2903
|
The following cache device has been registered.(wwn) %1 (path) %2 : FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2904
|
The following cache device has been removed.(wwn) %1 (path) %2 : FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2905
|
The following cache device is being removed.(wwn) %1 (path) %2 : FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2906
|
Caching is being removed for the following storage device.(wwn) %1 (path) %2 : FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1201, 1501
|
2907
|
Caching has been enabled on the following storage device.(wwn) %1 (path) %2 : FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1201, 1501
|
2908
|
The following cache device has been disconnected.(wwn) %1 (path) %2 : FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2909
|
The following storage device is in an unknown state.(wwn) %1 (path) %2 : FluidCache
|
Warning
|
Service is required. Contact Dell Technical Support.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1203, 1503
|
2910
|
Caching has been disabled for the following storage device.(wwn) %1 (path) %2 : FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1201, 1501
|
2911
|
The following cached LUN has had a failure.(wwn) %1 (path) %2 : FluidCache
|
Error
|
Service is required. Contact Dell Technical Support.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1404
|
2912
|
Resilvering for the following cache device is complete.(wwn) %1 (path) %2 : FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2913
|
The following failed cache device has completed recovery.(wwn) %1 (path) %2 : FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
901
|
2914
|
A valid permanent license is installed.: FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1601
|
2915
|
No valid license is installed.: FluidCache
|
Error
|
A valid license must be installed.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1604
|
2916
|
Running on an evaluation license. Days remaining %1 (days): FluidCache
|
Information
|
A permanent license should be purchased.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1601
|
2917
|
Running on an expired evaluation license. No configuration changes will be allowed. Expired days: % 1: FluidCache
|
Error
|
A permanent license must be installed.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1604
|
2918
|
Running on an expired evaluation license. Caching functionality is disabled. Expired days: % 1: FluidCache
|
Error
|
A permanent license must be installed
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1604
|
2919
|
Running on an expired/invalid license. Configuration changes are disabled.: FluidCache
|
Error
|
A valid permanent license must be installed
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1604
|
2920
|
A license has been installed.: FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1601
|
2921
|
A license has been removed.: FluidCache
|
Information
|
A license should be installed
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1601
|
2922
|
Not enough memory to run necessary services.: FluidCache
|
Error
|
You must run on a system with adequate memory.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1604
|
2923
|
One or more cache devices are missing. Cache is hung.: FluidCache
|
Error
|
To resolve the issue, insert the missing cache device. If the cache device was unplugged, reactivate it.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1604
|
2924
|
All cache devices have been found and registered.: FluidCache
|
Information
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1601
|
2930
|
Even though caching was enabled in write-back mode, it is currently operating in write-through mode.: FluidCache
|
Warning
|
To resolve the issue, add a PCIe SSD to the cache pool.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1203, 1503
|
2931
|
Even though caching was enabled in write-back or write-through mode, it is currently operating in pass-through mode.: FluidCache
|
Warning
|
To resolve the issue, add one or more PCIe SSDs to the cache pool.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1603
|
2932
|
Caching is no longer degraded to write-through mode and is now operating in write-back mode.: FluidCache
|
Warning
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1203, 1503
|
2933
|
Caching is no longer degraded to pass-through mode and is now operating in its configured mode.: FluidCache
|
Warning
|
No action required.
|
Clear Alert: None Related Alert: None
LRA Number: None
|
1203, 1503
|